 Post subject: Gas Boiler Problem
PostPosted: Wed Nov 19, 2025 12:48 pm 
Offline
User avatar

Joined: Tue Apr 23, 2024 3:29 pm
Posts: 2236
Location: Out in the sticks in Northumberland
If anyone can help, maybe by checking what your gas boiler is doing it would be much appreciated.

My gas boiler comes on for around 30 mins first thing in the morning, heats the water with 66 degrees being the the flow temp, hot water in cylinder is heated up to 60 degrees. Radiators warm up nicely and the boiler's temp after 30 mins goes to 67,68, 69, 70 within a few seconds and switches off.

The flow temp then falls to around 57/58 within 30 seconds, a few minutes later the boiler comes on and then is on for around 10-15 seconds, flow temp goes from 57 to 70 and then the boiler switches off. It then repeats this every 4 mins all day long.

Checked the cylinder thermostat that is working fine and it is closing the valve to the cylinder when 60 degrees is reached.
Room thermostat has been checked and that is fine.

Looked online and all I can find is that the boiler is short cycling and needs to be looked at.
Have booked up an engineer to call round later this week to check what is going on.

Just wondered what everyone else's boiler is doing when the CH is on?

My boiler is a glowworm condensing boiler for water and central heating.
Got the tank in the loft and the cylinder in the airing cupboard.

Hot water is fine and so are the radiators but I have never experienced the boiler doing this on/off every 4 mins.

Any help would be greatly received....


Top
 Profile  
 
 Post subject: Re: Gas Boiler Problem
PostPosted: Wed Nov 19, 2025 1:06 pm 
Online
User avatar

Joined: Sun Jan 03, 2010 10:11 am
Posts: 7410
Location: Rocks or Colliery?
Could be a faulty heat sensor, it's assuming it's dropping too quickly (or low temperature) and kicking in, most boilers now have inbuilt anti frost sensors so as soon as the temperature drops they perform a short cycle to keep the pump active and stop the water within the system from freezing. I suppose you could turn it off altogether if it's annoying but if not best to leave it on.

_________________
...and no regime can buy or sell me....


Top
 Profile  
 
 Post subject: Re: Gas Boiler Problem
PostPosted: Wed Nov 19, 2025 1:34 pm 
Offline
User avatar

Joined: Wed Jan 20, 2016 3:22 pm
Posts: 23139
just get a heat pump installed. you know it makes sense plus you can lecture us all about the bit you are doing to save mankind.


Top
 Profile  
 
 Post subject: Re: Gas Boiler Problem
PostPosted: Wed Nov 19, 2025 4:29 pm 
Offline
User avatar

Joined: Fri Aug 18, 2006 12:18 pm
Posts: 40908
accrington fan wrote:
just get a heat pump installed. you know it makes sense plus you can lecture us all about the bit you are doing to save mankind.

And experience the pleasure of a tepid shower :lol:

_________________
It’s what he does….. he’s a terrier.


Top
 Profile  
 
 Post subject: Re: Gas Boiler Problem
PostPosted: Wed Nov 19, 2025 5:45 pm 
Online

Joined: Wed Apr 26, 2023 3:07 pm
Posts: 6154
If it's only happened today could be condensate drain pipe is frozen, think it's common and particularly for boilers in lofts?


Top
 Profile  
 
 Post subject: Re: Gas Boiler Problem
PostPosted: Thu Nov 20, 2025 10:24 am 
Offline
User avatar

Joined: Tue Apr 23, 2024 3:29 pm
Posts: 2236
Location: Out in the sticks in Northumberland
Been doing this for a while, in fact since its last service last month.
Engineer is due round today so will find out what the problem is.


Top
 Profile  
 
 Post subject: Re: Gas Boiler Problem
PostPosted: Thu Nov 27, 2025 12:46 pm 
Offline
User avatar

Joined: Tue Apr 23, 2024 3:29 pm
Posts: 2236
Location: Out in the sticks in Northumberland
Well after several visits, it was found that the engineer who did the service left the kW too high instead of resetting it back to what it was when he left!

Also subsequent work to try and resolve the issues resulted in the sensors being incorrectly wired, which meant the boiler kettled and shut down leaving me with no CH and HW for a few days.

Also one of the engineers had not set the balancing and return valves up correctly resulting in an incorrect flow of heat through the system and finally I discovered today that the new cylinder thermostat which was fitted the other week, well the cap had been put on incorrectly so that the hot water was wanting to be heated up to 80 degrees instead of 60 degrees. I have corrected that by lining up the groove of the cap with the arrow of the dial.

Incompetence is probably too weak a word to use!!!

A strong complaint has gone in!

Company is British Gas with the homecare product for anyone interested who was to blame!!!!


Top
 Profile  
 
 Post subject: Re: Gas Boiler Problem
PostPosted: Thu Nov 27, 2025 1:41 pm 
Offline
User avatar

Joined: Wed Jun 24, 2009 7:59 pm
Posts: 13260
Snowy wrote:
accrington fan wrote:
just get a heat pump installed. you know it makes sense plus you can lecture us all about the bit you are doing to save mankind.

And experience the pleasure of a tepid shower :lol:


By tepid shower do you mean the government front bench or left wing zealots in general.

_________________
Come on Pools


Top
 Profile  
 
 Post subject: Re: Gas Boiler Problem
PostPosted: Thu Nov 27, 2025 3:07 pm 
Offline
User avatar

Joined: Sun Aug 13, 2017 8:27 am
Posts: 8621
Location: Stoke Bank
Stocksfield_Poolie wrote:
Well after several visits, it was found that the engineer who did the service left the kW too high instead of resetting it back to what it was when he left!

Also subsequent work to try and resolve the issues resulted in the sensors being incorrectly wired, which meant the boiler kettled and shut down leaving me with no CH and HW for a few days.

Also one of the engineers had not set the balancing and return valves up correctly resulting in an incorrect flow of heat through the system and finally I discovered today that the new cylinder thermostat which was fitted the other week, well the cap had been put on incorrectly so that the hot water was wanting to be heated up to 80 degrees instead of 60 degrees. I have corrected that by lining up the groove of the cap with the arrow of the dial.

Incompetence is probably too weak a word to use!!!

A strong complaint has gone in!

Company is British Gas with the homecare product for anyone interested who was to blame!!!!


That is no surprise given what a friend of mine who had his own business and then went to work for them for a short time.
Go independent by googling Gas Safe engineers in my area.

_________________
If it looks like a duck, swims like a duck and quacks like a duck it is probably a duck!


Top
 Profile  
 
 Post subject: Re: Gas Boiler Problem
PostPosted: Thu Nov 27, 2025 4:43 pm 
Offline

Joined: Wed Oct 24, 2012 9:49 pm
Posts: 2239
Location: Morpeth
Snowy wrote:
accrington fan wrote:
just get a heat pump installed. you know it makes sense plus you can lecture us all about the bit you are doing to save mankind.

And experience the pleasure of a tepid shower :lol:



Give over Snowy - you're becoming as repetitive as a Starmer lie - we've a heat pump and the shower is far from tepid.


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 10 posts ] 

All times are UTC [ DST ]


Who is online

Users browsing this forum: bobby lemonade, frankie1951, Hartleblue, jumbodabber, paulus the woodgnome and a side salad, poolie1966, PTID, Smokin Joe and 66 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group